Events are not showing or being logged.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Events are not showing or being logged.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3134 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Events are not showing or being logged.

Guinan AdamSteele Guinan
‎2019-07-25 03:02 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:41 AM

Issue

  • Controllers are online but events are not being logged.
  • No live event updates are showing in the All Events Status Page or being logged to the SecurityExpertEvents database.

Product Line

EcoStruxure Security Expert

Environment

Security Expert Client

Cause

Below is a list of the current causes that may contribute to the issues described:

  1. The Event Server settings are not configured correctly.
  2. The Firewall is blocking required communications ports.
  3. The default Save Events action has been removed.
  4. The All Events event filter has an Event Type or Record Filter attached to it which is filtering out events.

Resolution

For Cause 1

Confirm that the Download Server, Event Server, and Controllers are configured correctly. Check all of the items in this Troubleshoot Security Expert Controllers showing offline article.

For Cause 2

Check that any Firewalls are disabled or setup to allow all required ports through. See SX-SRVR Networking Guide for Administrators for further details. Also, confirm that any Anti Virus software is also not blocking required ports or Security Expert applications.

For Cause 3

In Security Expert go to Events > Actions and confirm that there is a Save Events action configured for the Site. The action will look like what is shown below and can be manually created if it is not present.

Figure 1 - Save Events ActionFigure 1 - Save Events ActionFigure 1 - Save Events Action

For Cause 4

Ensure that the Status Page view being used is able to see those events and is not filtered in any way.

Under Events > Event Filters check that the All Events Event Filter is not filtered and it is set to show all events and records. By default, this is not filtered and not able to be changed.

  • On the Event Types tab ensure "Include All Event Types" is selected.Figure 2 - Event Filter Event TypesFigure 2 - Event Filter Event TypesFigure 2 - Event Filter Event Types
  • On the Records tab ensure there is no record filter attached.Figure 3 - Event Filter - RecordsFigure 3 - Event Filter - RecordsFigure 3 - Event Filter - Records
  • Then check that the All Events event report is using the All Events filter for All Record Groups. Figure 5 - Event Reports All EventsFigure 5 - Event Reports All EventsFigure 5 - Event Reports All Events
  • Note that a fix for the database is available.  Please contact your local support to verify and provide a fix for this issue.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (5)
  • Find more articles tagged with:
  • AdamSteele19
  • AdamSteele21
  • AdamSteele23
  • IntLink_165904
  • RobertAndriolo21
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.