Estimated Values appear in Xenta logs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Estimated Values appear in Xenta logs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1272 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Estimated Values appear in Xenta logs

Picard Product_Support
‎2018-09-06 01:53 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:41 AM

Issue

When you view a Xenta Log through Vista you get estimated values in the Log.

Product Line

TAC Vista

Environment

Vista 4.x.x

Vista 5.x.x

Cause

If the site has many Xenta logs in 200,300 or 400 controllers you maybe exceeding the limit for trend uploads to Vista.

The maximum limit is 4 uploads of Xenta logs per minute to Vista.

If you exceed this value estimated values may appear in the Xenta logs.

Here is a link to a white paper description on this topic

TAC Xenta Trend Logs Whitepaper

Resolution

Here are some steps to check if the estimated values are caused from excessive Xenta trend upload.

 

Calculate the amount of uploads that are occurring in the database.

As an example if a Xenta log is set to store information in the controller for 1 hour and upload at 80% full.

This equates to 0.8 uploads per hour or 0.013 uploads per minute.

If you work out this rate for all the xenta logs in the database you can then calculate how many uploads are occurring per minute.

To extract all the Xenta Logs in the Vista database follow these steps also shown in the video.

  1. From TAC Vista workstation select View and then Search from the toolbar.
  2. select the browse option for the field "Type of devices or objects"
  3. Expand the heading labeled Files.
  4. Expand the heading labeled Trend Logs under the Files heading.
  5. Expand the heading labeled Trend Log Vista under the Trend Log heading
  6. Check the Trend Log Xenta box
  7. Select OK
  8. In the Property value dropdown list select the" Log size byte " option. This is the Xenta Log duration in seconds.
  9. Select the search Button
  10. The search results now show all the Xenta Logs. You may need to uncheck the "interrupt search if more than 1000 results" to capture all Xenta trends
  11. In the Search output Pane right mouse click and select "Additional properties"
  12. Expand the list and select "Retrieve at % Full option"
  13. The Search results then show all Xenta trends with Xenta Log duration and retrieve % full.
  14. Copy this list in Excel and calculate the uploads per minute from this Database.

Below is an image showing the data pasted into Excel, displaying the equation to calculate the upload per minute value per log: 

Excel Capture.bmp

If you find your total "uploads per minute" exceed 4 then reducing this may remove the estimated values.

Some ways to do this are.

  1. Extend the Xenta log storage time in the Xenta device if memory permits.
  2. Change the upload percentage to a greater number if it has been decreased below 80% 
  3. Increase the Xenta sample rate which will allow for the Xenta storage to be extended as in point 1.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5200
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore