Escort or double card swipe required at a door.
  • Escort or double card swipe required at a door.
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
‎2018-09-06 10:38 AM
Does Continuum support Escorted or double card swipe requirements?
ACX57xx, AC1 range
Some specifications call for 2 valid cards to be presented before the door is released, also called the 2 man rule.
Continuum does not support the requirement for escorting or double card swipe requirements, if a valid card is swiped at a door it will release.
One possible workaround could be to have 2 readers (doors) each opening an output relay. Then wire the two relays in series, such that both outputs need to be On to power the door magnetic lock.
So the personnel and the supervisor (or Escort) both need to present their card to their respective readers at the same time to open the door.
  • 12600