Error
"An error was detected during the creation of a remote refresh cached object
Unable to find an object in the database"
Seen when creating the EventNotification Template
Continuum
  • Templates
  • Event Notification
Error
Seen when creating the EventNotification Template and modifying Ack Required or Priority before pressing "OK"
The error is not always seen but a simple work around is to press "OK" before editing the template.
Then re-open and modify the template as required
- This issue has been reported to engineering and is being evaluated for correction in a future revision
NOTE - This was a minor issue and was fixed by version 1.94