Error reloading doors after Continuum upgrade from pre 1.8 version.
  • Error reloading doors after Continuum upgrade from pre 1.8 version.
  • AbeMeran
    AbeMeran
‎2018-09-06 10:38 AM
After upgrading the database from version 1.74 to 1.81 and converting the NC1 to NC2 all the doors produce the following error on reload.
Infinity controller error: Feature has not been enabled in this controller  An error was detected while attempting to set an attribute in a remote Infinity object.
CyberStation
CX9680
ACX5720
ACX5740
New CardFormats2 column in the door table contains incorrect value.
Sending a door object from the database to a text file shows the following
InstanceId : 7001/7004
 CardFormats : 4
 CardFormats2 : 1246576928 <------------------------ this attribute should have an initial value of zero.
 Description : DOOR 1.04
Run the following SQL query to set the initial value of the new CardFormats2 column in the database to zero
update Door Set CardFormats2 = 0
  • 12604