Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Error, "Unknown SMTP Host: smtp.broadband.rogers.com" when attempting send email message from an I/A Series UNC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error, "Unknown SMTP Host: smtp.broadband.rogers.com" when attempting send email message from an I/A Series UNC.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3443 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error, "Unknown SMTP Host: smtp.broadband.rogers.com" when attempting send email message from an I/A Series UNC.

Picard Product_Support
‎2018-09-06 03:55 PM

Issue

I have a UNC-520-2 running Niagara 522 that is connected on a local network, with internet access. Alarm emails are not sent and I get the following error message:

ERROR: Cannot send mail [/Dundee_2StClair/services/MailService]
javax.mail.SendFailedException: Sending failed;
nested exception is:
javax.mail.MessagingException: Unknown SMTP host: smtp.broadband.rogers.com ;
nested exception is:
java.net.UnknownHostException
at javax.mail.Transport.send0 (bytecode 611)
at javax.mail.Transport.send (bytecode 9)
at tridium.services.MailService.sendImpl (bytecode 29)
at tridium.services.MailService.run (bytecode 44)
at java.lang.Thread.run (line 5)

Environment

I/A Series R2 UNC (520, 410 or JACE-NSX/NXT)

Cause

Mail server address defined by name (smtp.broadband.rogers.com)

No DNS server addresses defined in the IP address configuration of the UNC

Resolution

The error message indicates that there was no response from the SMTP server address specified.  In this case, since the SMTP server is specified by name instead of its IP address, it is necessary to provide one or more DNS (Domain Name Service) servers that can be used to resolve the address to its associated IP address.

To enter one or more DNS addresses, access the UNC via the Admin Tool and select the Network Settings tab. On the lower part of the Network Settings screen, click the [Add] button and enter the IP address of the DNS server in the table.  Repeat this step if additional DNS servers are to be added.  Click the [Apply] to save the settings.  Here is what the screen looks like when two public DNS server addresses have been entered.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7649
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore