Error: "Infinity controller error: File took too long to open" when trying to save a program in the Plain English editor
  • Error: "Infinity controller error: File took too long to open" when trying to save a program in the Plain English editor
  • Jeff
    Jeff
‎2018-09-06 02:59 PM
When trying to save a program in the Plain English editor, you receive the message "Infinity controller error: File took too long to open"
This is typically caused because the program in the controller is busy executing a command that cannot be interrupted.
A workaround for this issue is:
  1. Right-click within the PE panel of the editor
  2. Clicking "Configuration..."
  3. Set the program state to Disabled, click OK
  4. Save your program
  5. Repeat the steps above but select Enabled and then click OK
  • 2547
100% helpful (2/2)