Error "Communication Error Exception has been thrown by the target of an invocation"
  • Error "Communication Error Exception has been thrown by the target of an invocation"
‎2018-09-11 12:55 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:41 AM
Error when trying to add exceptions to a schedule is seen when trying to "apply" the changes.
Example:
Personnel Manager
Error saving data
Communication Error Exception has been thrown by the target of an invocation.
The personnel object was created
Andover Continuum
Continuum
Too many old exceptions in the schedule.
Sometimes RPC (Remote Procedure Call) errors happen on Cyberstation following the above error.
Delete the old exceptions. This must be done manually for infinet schedules.
1.94 NOTE: If this issue is happening for 1.94, there is Hotfix for TPA CONT 12 0002.00 Schedule Exception Errors.zip that has been released for this issue.
The V1.94 issue is also detailed in Technical bulletin: TPA-BOST-12-0002.00
Hotfix+for+TPA_CONT_12_0002.00_Schedule_Exception_Errors.zip