Error number: 17040 Error description: Invalid format. (Subsystem: LNS, #40)
  • Error number: 17040 Error description: Invalid format. (Subsystem: LNS, #40)
‎2018-09-07 03:39 AM
  • Error number :      17040
  • Any tab except "Status" has some strange values. Trying to view or edit some values results in this error.
  • Xenta 102-AX Plug-in
  • Xenta 104 Plug-in
  • LonMaker
  • NL220
A value inside the device has been set with an invalid value.  It could be through an LNS browser, through an M/STAT or just through some glitch when setting a parameter.
The device will need to be recommissioned using default values.
  1. CAUTION:  Recommissioning a device with default values will erase any user defined configuration parameters.  Record all important data for the box:  duct area, airflow setpoints, operating parameters, etc.
  2. Right-click on the device in the LNS Management tool.  In LonMaker, select Recommission. In NL220, select Repair.
  3. Choose "Manufacturer Defaults" for the initial values.  Click OK.
  4. Launch the plug-in again.  The values should now be able to be changed to the desired value.