Error message when renaming some BACnet objects in Cyberstation.
  • Error message when renaming some BACnet objects in Cyberstation.
  • Jeff
    Jeff
‎2018-09-06 03:00 PM
When right clicking on some BACnet objects within Cyberstation (like EventEnrollments and Schedules) and clicking on "Rename", you may receive the following error message when you click Finish:
"Cannot set the Name. An attempt has been made to write to a BACnet property with a value that is outside the range of values defined for the property."
CyberStation
This issue occurs when you specify a Name that does not conform to Alias constraints (16 characters, letters, numbers, period, and underscore only).
Rename the object through its properties page to work around this limitation.