Reloading ACX2/NC2 produces error when reloading the following system variables
  • AllowedCreds
  • PersRecordCount
  • PIVReaderFormat
CyberStation
ACX5720
ACX5740
CX9680
Warning
The system variables in question (AllowedCreds, PersRecordCount, PIVReaderFormat) only apply to versions 1.1xxxxx and 2.1xxxxx of the ACX2 and NC2 respectively.
  1. Make sure the controller is running the appropriate version of the firmware.
  2. If the problem persists even with the correct firmware version then...
    1. Export the controller to text file
    2. Edit the dump file and remove ALL system variables
    3. Delete the controller
    4. Import the file to re-create the controller (the system variables will be created when the controller is created)
    5. Reload the controller, the errors should not longer appear.