Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Error importing I/NET sav file to XBuilder

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error importing I/NET sav file to XBuilder
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1293 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error importing I/NET sav file to XBuilder

Picard Product_Support
‎2018-09-06 02:26 PM

Issue

Error importing I/NET sav file to XBuilder

Environment

XBuilder

I/NET sav file import

Cause

There's a problem in how the DcuXml.exe and XBuilder handles the import of sav files. If the "home" folder of the Windows user you are logged in with has a ".", XBuilder will import the sav file to the I/NET folder alright, but will actually look for the sav file in the Files folder, so one folder back. Eg.

Domain user: br Location of the copied sav file:
C:\Documents and Settings\br\Local Settings\Temp\XBuilderPrj\PROJECTNAME\Files\INET
(For Win7 & Win Server 2008, it should be C:\Users\br\AppData\Local\Temp\XBuilderPrj\PROJECTNAME\Files\INET. You need to turn on the Show hidden File option in Folder and search options under the Organize menu )

Where XBuilder looks for the sav file:
C:\Documents and Settings\br\Local Settings\Temp\XBuilderPrj\PROJECTNAME\Files\INET
(For Win7 & Win Server 2008, it should be C:\Users\br\AppData\Local\Temp\XBuilderPrj\PROJECTNAME\Files\INET)

Local user: br Location of the copied sav file:
C:\Documents and Settings\br.WSDKHER9562\Local Settings\Temp\XBuilderPrj\PROJECTNAME\Files\INET
(For Win7 & Win Server 2008, it should be C:\Users\br.WSDKHER9562\AppData\Local\Temp\XBuilderPrj\PROJECTNAME\Files\INET)

Where XBuilder looks for the sav file:
C:\Documents and Settings\br.WSDKHER9562\Local Settings\Temp\XBuilderPrj\PROJECTNAME\Files
(For Win7 & Win Server 2008, it should be C:\Users\br.WSDKHER9562\AppData\Local\Temp\XBuilderPrj\PROJECTNAME\Files)

Resolution

XBuilder will generate an error, and the import.xml will be locked by the DcuXml.exe process, so you manually have to stop that. What you have to do is manually copy the sav file to the PROJECTNAME\Files directory before you import the I/NET network.

Labels (2)
Labels:
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3953
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore