Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Error: Prohibit to retain both Value and priority properties at same time

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error: Prohibit to retain both Value and priority properties at same time
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1717 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error: Prohibit to retain both Value and priority properties at same time

Administrator DavidFisher Administrator
‎2020-03-27 06:52 AM

on ‎2020-03-27 06:52 AM

Issue

Attempting to set the Retain Level attribute of a Value object results in the following error:

prohibit-to-retain-both-value-and-priority-properties-at-same-time.png

Saving Changes
Invalid data
'Prohibit to retain both Value and priority properties at same time: (point name)
Invalid data

Product Line

EcoStruxure Building Operation

Environment

EcoStruxure Building Operation 3.1

Cause

Prior to EBO 3.1, it was possible to set retention levels on both the Value attribute and individual members of the Priority Stack. Starting with 3.1, that is not allowed and will give this error if you attempt to change the retain level setting of a Value that already has it set on a Priority, or vice versa.

For systems configured in EBO 3.0 or prior that are upgraded to 3.1, the now invalid double-retention will be resolved automatically during the upgrade by retaining the Priority Stack retention level and setting the Value attribute Retain Level to No.

Resolution

Only set the retain level on one attribute of an object. The best attribute to retain is the Value. Setting Retain Level to Cold Start or Warm Start on the Value will also retain the full priority stack on a power failure or restart. Check the retain levels of each member of the priority array and ensure all are set to "No" and then set the Retain Level of the Value attribute to "Cold Start" or "Warm Start."

To clear the retain level of individual priorities:

  1. Open point's Property window
  2. Click the Command tab
  3. Click the gear icon next to a Priority level, most likely starting with Priority 16.
    priority-retain-level.png
  4. Check the checkbox for Retain level and set to No.
    retain-level-options.png

To set the retain level on the Value attribute:

  1. Open point's Property window
  2. Click the gear icon next to the value
    value-retain-level.png
  3. Check the checkbox for Retain level and choose the desired level.
    retain-level-options.png
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidFisher20
Was this article helpful? Yes No
0% helpful (0/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore