Error: NS #67 lcaErrNsSubnetDblimit
  • Error: NS #67 lcaErrNsSubnetDblimit
  • Sacco
    Sacco
‎2018-09-07 03:42 AM
The network subnet limit (currently 255) has been reached.
LNS
LonMaker
Vista
NL220
Run the LNS Database Recovery Wizard: If you are recovering through a PCC-10, PCLTA-10 or PCLTA-20, use the LonWorks Plug 'n Play Control Panel to select the NSI NI Application. Otherwise, error "NS #138 (Local interface is in the wrong state (unconfigured)" is reported, then "NS #67 system is not open)", then "LNS #55". Finally, the LNS Database Recovery Wizard only gives you the option to cancel the recovery.