An operation requiring a Neuron ID was attempted on a device with no Neuron ID.
Subsystem; NS #37
LNS
LonMaker
Vista
NL220
For example, if you invoke the Wink method on a device whose Neuron ID has not been set in the LNS database, this exception will be thrown.  In some other cases, this exception may be thrown if a device’s Neuron Id has been set in the LNS database, but the device has not been commissioned.
For example, if you read the SelfDocumentation property of a device before that device has been commissioned, this exception will be thrown, regardless of whether or not the device’s Neuron ID is set.
Make sure the Neuron ID has been set and the device is commissioned.