Error: NS #187 lcaErrNsSysimageUpgradeMemoryFailur
  • Error: NS #187 lcaErrNsSysimageUpgradeMemoryFailur
  • Sacco
    Sacco
‎2018-09-06 02:22 PM
New system image memory fails during upgrade.
LonMaker
NL220
Vista
LNS
This error will be generated if there is a failure to write the new system image the device after the LoadEx method has been invoked. These failures usually occur because the device does not have flash memory in the required location to hold the new image during the download process.
The old system image will remain intact if this error is thrown.  However, the device will remain applicationless.  You should load a new application image into the device with the Load or LoadEx methods in this case.
  • 4159