Error: NI #23 lcaErrNiVniInitFailure (Subsystem: NI, #23)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error: NI #23 lcaErrNiVniInitFailure (Subsystem: NI, #23)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1663 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error: NI #23 lcaErrNiVniInitFailure (Subsystem: NI, #23)

Picard Product_Support
‎2018-09-07 03:40 AM

Issue

Could not initialize the LonTalk stack.

Environment

LNS
NL220
LonMaker
Vista

Cause

Could not initialize the LonTalk stack.

Resolution

First, close the LonMaker tool, then test your network interface using the LonWorks Plug 'n Play utility found in the Windows Control Panel. Once there, press the "Diagnostics" button and then press the "Test" button. If you get a "Failed" message similar to the following:

------------------------------------------------------------------------------

LonWorks® PCC10/PCLTA10/PCLTA20 Device Driver

Version: 2.01

Card Type: PCLTA-20 / LMPA

Driver Status:

          Number of Free LTA Output Buffers-

           Non-Priority: 0, Priority: 0

          Loaded Image Size: 16384

          Interrupt Count: 17333

------ Network Interface Node Status ------

** Failed **

------------------------------------------------------------------------------

Then go back to the main LonWorks Plug 'n Play dialog and change your NI Application to something other than what is currently selected. Click on the "apply" button and do the test again. Don't forget to change it back to its original NI Application. Remember that the LonMaker tool can work with either the "NSI" or "VNI" NI Application images, although "VNI" is preferred due to higher performance.

You may also want to try to "reset" and "restart" your network interface card and driver from the "Diagnostics" window.

Once you stop getting the "Failed" message and see the network interface statistics, you should be able to open the network from the LonMaker tool. The following is an example of a successful "Test" result. Some of the counts may not be zero, but that should not be a problem unless it increases rapidly as you test again and again. If that happens, it can be due (most of the time) to one of three problems: wiring connections, excessive noise, or excessive traffic on the network.

------------------------------------------------------------------------------

LonWorks® PCC10/PCLTA10/PCLTA20 Device Driver

Version: 2.01

Card Type: PCLTA-20 / LMPA

Driver Status:

          Loaded Image Size: 57344

          Interrupt Count: 20345

------ Network Interface Node Status ------

CRC Errors:                  [00000]

TX Timeouts:                 [00000]

Lost (APP) Messages:         [00000]

Missed (NET) Messages:       [00000]

Most recent error:           0

Reset Cause:                 External

------------------------------------------------------------------------------

 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4214
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore