Error: LNS #55 lcaErrCantRecoverNotNewDb
  • Error: LNS #55 lcaErrCantRecoverNotNewDb
  • Sacco
    Sacco
‎2018-09-07 07:21 PM
A call to the RecoverFromNetwork method has been made, using a previously used network database.
LonMaker
NL220
Vista
LNS
For the recovery process, a newly created network database is required.
Run the LNS Database Recovery Wizard: If you are recovering through a PCC-10, PCLTA-10 or PCLTA-20, use the LonWorks Plug 'n Play Control Panel to select the NSI NI Application. Otherwise, error "NS #138 (Local interface is in the wrong state (unconfigured)" is reported, then "NS #67 system is not open)", then "LNS #55". Finally, the LNS Database Recovery Wizard only gives you the option to cancel the recovery.
see also Echerlon support article 190
  • 4186