Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Error: LNS #25 lcaErrDatabase

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Error: LNS #25 lcaErrDatabase
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Benji
    Benji
  • Product_Support
    Product_Support
  • Omaelk
    Omaelk
  • DavidFisher
    DavidFisher
  • Sacco
    Sacco

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2445 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Error: LNS #25 lcaErrDatabase

Picard Product_Support
‎2018-09-07 03:48 AM

Last Updated: Janeway Omaelk ‎2022-10-19 04:20 AM

Issue

An unexpected database error occurred.

"There can only be one LCA Object Server ActiveX control per process. Please make sure that you only have a single Object Server control in this process."

"Could not listen on _poet/tcp: The address is already in use or another server already running. (-2532)"

Environment

LonMaker
NL220
Vista
LNS

Cause

Microsoft Exchange 2003 Server and other OEM software sometimes use TCP ports 6001 or 6002. This causes a conflict since the POET server (FastObjects DB) defaults to TCP ports 6001 and 6002.

Resolution

For an automated solution, refer to: https://community.se.com/t5/TAC-Vista-Forum/LonMaker-POET-Port-Changer/td-p/271427

 

For a full explanation from Dialog Semiconductor, refer to: https://edgesupport.diasemi.com/hc/en-us/articles/206494283

 

Further details

 

Check that the ports used by LNS are not being blocked (firewalled) or used by another application. To verify this, type in the following command from a DOS prompt:

netstat -bn

You should now get a list of in-use TCP ports. Look for an entry saying {your computer name}:6001 or 6002. If you find one, you have located a conflict and you will need to change the POET Port numbers.

Check if you run a firewall on this PC. If yes, you need to find the list of Programs with their Internet Access level and make sure you have given access to the appropriate files. To run LonMaker/LNS , you need to give access to ptserv32.exe, LonMaker.exe, lonpoint.exe, visio.exe, lmwbrw32.exe and lsass.exe.

You can modify the ports used by the POET server and clients by modifying the "Services" file (%WINDIR%\System32\Drivers\Etc\Services) using a text editor like Wordpad.exe or Notepad.exe.

For example, to change the POET port numbers to 7001 and 7002, add/modify the following lines in the "Services" file. The  '#' in the example indicates that the following text is a comment.

For Win XP: use "Windows\System32\Drivers\Etc\Services". If you see the "poet" and "_poet" entries, go ahead and change the port numbers from 6001 and 6002 to 7001 and 7002.

If you don't see these entries, simply add the lines below.

poet          7001/tcp    #FastObjects services

_poet        7002/tcp    #FastObjects services

https://echelon.force.com/support/s/search/All/Home/562?tabset-95728=2

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4182
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore