Error: LNS #102 lcaErrNeuronIdInUse. Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LNS, #102)
  • Error: LNS #102 lcaErrNeuronIdInUse. Attempt to assign a neuron ID that is already in use by another device. (Subsystem: LNS,...
  • Sacco
    Sacco
‎2018-09-06 02:21 PM
The Neuron ID assigned is already being used by another device in the network.
LonMaker
NL220
Vista
LNS
If you are typing in the Neuron ID manually, check to make sure a device actually does have that neuron ID already.  If you are service pinning and you are certain that no other device is using that Neuron ID, then it may be a “phantom node” that will come to the surface by attempting a resynch.  You can then delete that phantom node and proceed.
  • 4193