Error 80041195, Info: Communication port not connected
  • Error 80041195, Info: Communication port not connected
‎2018-09-09 11:29 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:41 AM
When downloading a programmable controller with the Vista system plug-in, the process fails and reports the Error 80041195, Info: Communication port not connected.
NOTE: Error 80041195 has also been reported when performing a commence communication command in the Vista system plug-in.
TAC Vista
  • Vista Server 5.1.5
  • Vista System Plug-In 5.1.5
Vista Server 5.1.5 is not communicating to the LNS server properly
Vista Server hotfix 14 addresses this error within Vista Server 5.1.5.
  1. Download TAC Vista Server 5.1.5 Hotfix 14 from The Exchange Download Center.
  2. Run the TACVista515HotFix51514.exe file.
  3. Reboot the machine.
This error has also been observed If the PC is running a a 64-bit operating system which is not supported for LonMaker or NL220. See Echelon LonMaker and Newron NL220 on 64-bit operating systems for more information.
  • 5401
0% helpful (0/1)