Enterprise server is unable to communicate with the Report server
  • Enterprise server is unable to communicate with the Report server
  • sesa177673
    sesa177673
‎2018-09-06 10:30 AM
Report server is unable to communicate with the Enterprise Server (ES). After configuring the reports server and then adding the report server to the ES (under -servername-\System\Report Manager) the "Reports" folder does not get added to the ES. It is however possible to log in to the Report server using the URL.
The SmartStruxure reporting agent is running, the SQL installation is complete and working but nothing is logged in the SQL report database.
StruxureWare Building Operation 1.X.0
SmartStruxure WebReports
Incorrect proxy settings on the network.
Correct the proxy settings, which may well be controlled centrally by the IT department.