Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Enable a Sigma controller to broadcast more than 50 globals (bit mask)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enable a Sigma controller to broadcast more than 50 globals (bit mask)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2107 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enable a Sigma controller to broadcast more than 50 globals (bit mask)

Product_Support
‎2018-09-07 08:23 PM

Last Updated: CraigEl Champion ‎2025-10-07 07:33 PM

Issue

How can more than 50 globals be transmitted from a Sigma controller when there are many digital object states to share between controllers?

Product Line

Satchwell BAS & Sigma

Environment

Sigma Controller (all)

Cause

Sigma controllers are inherently limited to broadcasting a maximum of 50 global variables.

Resolution

To overcome the 50-global limit, you can encode multiple digital object states into a single analogue value using a binary count method. This allows up to 16 digital states to be represented and transmitted as one global analogue value.


This method leverages the MASK command in Sigma programmable objects to decode the analogue value back into individual digital states.


Implementation Steps

  1. Create a Programmable Object in the Transmitting Controller

    • Use binary counting to combine up to 16 digital objects into a single analogue value.
    • Each bit in the binary representation corresponds to the on/off state of a digital object.
    • An analogue value of 901 represents the binary value 0000001110000101, where each bit (1 or 0) indicates the state of a digital input (DI) object.

    Example:
    Create a program object in the transmitting controller that 'binary' counts up to 16 digital objects:

    10 XINT = 0
    20 IF POINT 0|180 ON THEN XINT = XINT + 1 1st condition
    30 IF POINT 0|181 ON THEN XINT = XINT + 2 2nd condition
    40 IF POINT 0|182 ON THEN XINT = XINT + 4 3rd condition
    50 IF POINT 0|183 ON THEN XINT = XINT + 8 4th condition
    60 IF POINT 0|206 ON THEN XINT = XINT + 16 5th condition
    70 IF POINT 0|207 ON THEN XINT = XINT + 32 6tht condition
    80 IF POINT 0|208 ON THEN XINT = XINT + 64 7th condition
    90 IF POINT 0|209 ON THEN XINT = XINT + 128 8th condition
    100 IF POINT 0|210 ON THEN XINT = XINT + 256 9th condition
    110 IF POINT 0|214 ON THEN XINT = XINT + 512 10th condition
    120 IF POINT 0|215 ON THEN XINT = XINT + 1024 11th condition
    130 IF POINT 0|216 ON THEN XINT = XINT + 2048 12th condition
    140 IF POINT 0|217 ON THEN XINT = XINT + 4096 13th condition
    150 IF POINT 0|218 ON THEN XINT = XINT + 8192 14th condition
    160 IF POINT 0|202 ON THEN XINT = XINT + 16384 15th condition
    170 IF POINT 0|203 ON THEN XINT = XINT + 32768 16th condition
    180 XFLO = FLOAT ( XINT )
    190 RETURN VIA TEXT 153 VALUE XFLO
  2. Set Up Bit Masking in the Receiving Controller

    • In the receiving controller create up to 16 programmable objects to decode the transmitted analogue value.
    • Use the MASK command to extract individual digital states from the binary representation.
      1st load
      10 XINT = NINT POINT 0|222
      20 YINT = XINT MASK ( 1 )
      30 IF YINT = 1 THEN RETURN TRUE "load 1 on"
      40 RETURN FALSE "load 1 off"
      --------------------------------------------------------------
      2nd load
      10 XINT = INT POINT 0|222
      20 YINT = XINT MASK ( 2 )
      30 IF YINT = 2 THEN RETURN TRUE "load 2 on"
      40 RETURN FALSE "load 2 off"
      --------------------------------------------------------------
      3rd load
      10 XINT = INT POINT 0|222
      20 YINT = XINT MASK ( 4 )
      30 IF YINT = 4 THEN RETURN TRUE "load 3 on"
      40 RETURN FALSE "load 3 off"
      --------------------------------------------------------------
      4th load
      10 XINT = NINT POINT 0|222
      20 YINT = XINT MASK ( 8 )
      30 IF YINT = 8 THEN RETURN TRUE "load 4 on"
      40 RETURN FALSE "load 4 off"
      --------------------------------------------------------------
      5th load
      10 XINT = NINT POINT 0|222
      20 YINT = XINT MASK ( 16 )
      30 IF YINT = 16 THEN RETURN TRUE "load 5 on"
      40 RETURN FALSE "load 5 off"
      --------------------------------------------------------------
      6th load
      10 XINT = NINT POINT 0|222
      20 YINT = XINT MASK ( 32 )
      30 IF YINT = 32 THEN RETURN TRUE "load 6 on"
      40 RETURN FALSE "load 6 off"
      --------------------------------------------------------------
      7th load
      10 XINT = NINT POINT 0|222
      20 YINT = XINT MASK ( 64 )
      30 IF YINT = 64 THEN RETURN TRUE "load 7 on"
      40 RETURN FALSE "load 7 off"
      --------------------------------------------------------------​

    🔗 Click here for detailed setup instructions

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4852
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore