Editing large numbers of links and bindings on multiple TGML graphics

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Editing large numbers of links and bindings on multiple TGML graphics
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2253 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Editing large numbers of links and bindings on multiple TGML graphics

Picard Product_Support
‎2018-09-10 03:15 AM

Issue

Creating many TGML graphics that use the same or similar links and bindings can be difficult and time consuming.

Environment

  • TGML
  • Vista Workstation

Cause

The copy and paste feature does not work on more than one link at a time.

Resolution

Whenever a Vista database export is performed on a group of TGML graphics, a .zip file is created that contains a source TGML file for each selected graphic, and one XML file describing all of the links and bindings contained in the database for those graphics. By editing this XML document and leveraging find/replace capabilities of text editors, the process of manually populating links and bindings can be sped up substantially.

Warning: Always back up your database before performing any manipulation of XML files. There is a potential for your graphics to be ruined if a mistake is made, so be sure a current backup is available in this event. This is an advanced operation and should only be attempted by individuals with an understanding of Vista TGML graphics.

This example shows how to populate the links on a standard menu that appears on every TGML graphic in a database. For simplicity, the database has three graphics: AHU1, AHU2, and AHU3. But the steps can be applied to hundreds of graphics just the same.

  1. A menu is created in TGML with a link to each graphic. The links are named AHU1, AHU2, and AHU3. These will correspond with the TGML objects in Vista that are also named AHU1, AHU2, and AHU3. The names do not have to match, but it is a good design standard to follow whenever possible.
  2. Right-click on the first graphic and choose Open Links Window. The first graphic should be populated manually to give a template for the rest. Populate each link using the traditional drag-and-drop. Verify the links are populated correctly.
  3. Go to File > Database > Export.... Select "Get a customized copy of the database.
     This is the only option that needs to be selected.
  4. Highlight all of the graphics and drag them into the Export window. Click the green arrow in the upper-lefthand corner of the Export window and give the .zip file a name. Click Save. A message will appear stating "Vista Database Export completed"
  5. Find the resulting .zip file in the location specified in Step 4. Right-click and extract all files. Depending on the operating system and software, this step may vary. Unzip the specified file.
  6. In the resulting folder, find VistaDbImportExport.xml. Right click and open with Notepad or other text editor.
  7. Find Objects of type "TGML_LINK." If the RELREFID is populated, then this link has a destination. If it says RELREFID="" then this link is not yet populated.
  8. Time for some strategic find/replace. In this example, AHU1 has all of the links populated. But AHU2 does not. There are three links on each page that all share the same destination.
    Find the populated entry for AHU1 links:

    Object TYPE="TGML_LINK" NAME="AHU1.AHU1" DESCR="" SHCP="" SHCR="" IOLABEL="" RA="" WA="" KEYLABEL="" RELREFID="Graphics-AHU1" _PROTECTED="0"

    Find the non-populated entry for AHU1 links:

    Object TYPE="TGML_LINK" NAME="AHU2.AHU1" DESCR="" SHCP="" SHCR="" IOLABEL="" RA="" WA="" KEYLABEL="" RELREFID="" _PROTECTED="0"
     
  9. Select everything after the graphic name that is not unique and perform a find replace:

    Find:
    AHU1" DESCR="" SHCP="" SHCR="" IOLABEL="" RA="" WA="" KEYLABEL="" RELREFID=""

    Replace:
    AHU1" DESCR="" SHCP="" SHCR="" IOLABEL="" RA="" WA="" KEYLABEL="" RELREFID="Graphics-AHU1"
     
  10. Repeat this action for AHU2 and AHU3.
  11. When all of the edits have been made to the XML document, save and close it.
  12. Highlight the XML document as well as all of the TGML files in the unzipped folder. Right click and select Send to > Compressed (zipped) folder. This will create a modified database export file.
  13. In Workstation, go to File > Database > Import. Browse to the .zip file created in Step 12. De-select Perform alarm refresh and hit OK. A message will be displayed that says "Vista Database Import completed.
  14. All of the links on every page are now populated.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6303
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of