Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Echelon LON interface card installed in computer is not recognized by the LonWorks Plug and Play utility nor by the I/A Series software installed on the computer.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Echelon LON interface card installed in computer is not recognized by the LonWorks Plug and Play utility nor by the I/A Serie...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2291 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Echelon LON interface card installed in computer is not recognized by the LonWorks Plug and Play utility nor by the I/A Series software installed on the computer.

Picard Product_Support
‎2018-09-06 02:50 PM

Issue

Echelon LON interface card installed in computer is not recognized by the LonWorks Plug and Play utility nor by the I/A Series software installed on the computer.

Environment

  • LON interface card
  • PC

Cause

This problem is caused by not installing the Echelon driver for the PCLTA-10 / PCLTA-20 / PCLTA-21 / PCC-10 card before installing the card into the computer.

Resolution

Steps 14-20 of this procedure can be used to test the PCC-10 lon card and driver if the proper driver is believed to be installed.  
 

Before attempting to reinstall the driver, verify that this Echelon file is available:  "OpenLDV340.exe", "153-0117-01C.zip" or "PCLTA21 Win2k XP.exe". If the .zip version is available, extract the .exe file from that .zip file, to the desktop.
 

To correct the problem and install the proper driver, use the following procedure.

  1. Open the Windows Control Panel and select SYSTEM then select the hardware tab.
  2. Select the Device Manager button.
  3. Check to see if the Echelon card is already installed -- look for the entry "Lonworks Network Interface" and click on that entry to open it then select the "Lonworks xxxx Network Interface" choice that was just displayed. (then continue with step 5 below.)
  4. If the Lonworks Network Interface was not shown, look for an entry with a yellow question mark -- a Lonworks entry so marked should be found. Select that entry.
  5. Right click on the Lonworks entry just selected and select "Uninstall…". Follow the prompts to uninstall the driver.
  6. Shut down Windows and power down the computer then remove the Echelon card from the computer.
  7. Power up the computer.
  8. Log into the computer using an account with full administrative rights. Run the Lonworks driver application file ("OpenLDV340.exe", "153-0117-01C.zip" or "PCLTA21 Win2k XP.exe") that was downloaded and extracted. This installs the driver into Windows.
  9. After the installation completes, close the prompt indicating that a reboot is required then shut down Windows and power down the computer.
  10. Reinstall the LON interface card.
  11. Power up the computer and log into Windows.
  12. The system will indicate that new hardware has been installed and will attempt to locate a driver for the new hardware. Allow the system to install the card driver.
  13. When the hardware installation wizard finishes, it may indicate that the computer must be restarted before attempting to use the new hardware. If so prompted, shut down windows and restart the computer, logging in again as an administrative user.
  14. Open the Windows Control Panel and select (double click) the "Lonworks Plug 'n Play" entry.
  15. Verify that the device selected is LON1.
  16. If not already selected, specify the NSIxxx application in the NI Application selection box.
  17. Click the "Diagnostics" button.
  18. Click the "Reset" button then click the "Restart" button. Click "Yes" to reset the card to its boot state.
  19. Click the "Test" button and verify that no errors are indicated.
  20. Click the "OK" button to leave the Diagnostics screen then click "OK" on the Lonworks Plug 'n Play screen to save the configuration information and exit the utility.

The Echelon LON Interface Card is now ready to use.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2946
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of