Issue
When editing a Script program, the Automation Server or Enterprise Server crashes when clicking "Save." After that, the connection is never restored to the server. The server needs to be formatted, software reloaded, and a backup restored to it.
Product Line
EcoStruxure Building Operation
Environment
SmartStruxure 1.0.0 to 1.5.0
Cause
In SmartStruxure 1.5.0 and earlier, publics were not supported in Script functions although they could be used. If used, the server will crash in some cases and render the database unusable.
Resolution
The workaround is to not use publics in Script functions in the affected versions. The issue is solved from version 1.6 RC.