ENC is licensed for Microsmart but gets error "Unlicensed: javax.baja.license.FeatureNotLicensedException: tac_llc:tacms" when attempting to access the Microsmart Network...

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • ENC is licensed for Microsmart but gets error "Unlicensed: javax.baja.license.FeatureNotLicensedException: tac_llc:tacms" whe...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1377 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ENC is licensed for Microsmart but gets error "Unlicensed: javax.baja.license.FeatureNotLicensedException: tac_llc:tacms" when attempting to access the Microsmart Network...

Picard Product_Support
‎2018-09-10 03:33 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:40 AM

Issue

ENC is licensed for Microsmart but gets error "Unlicensed: javax.baja.license.FeatureNotLicensedException: tac_llc:tacms" when attempting to access the Microsmart Network property sheet.

Environment

I/A Series G3, ENC-520 with TAC-LLC license installed.

Cause

When displaying the I/A Series G3 Platform details via the Platform Administration screen in the Workbench, the display shows the following for licensing:

Licenses
  Tridium.license (Tridium 3.5 - never expires)
  TAC_LLC.license (TAC_LLC 3.5 - never expires)

Certificates
  Tridium.certificate (Tridium - never expires)

This information shows that the Tridium and TAC_LLC licenses have been installed but only the Tridium certificate. The TAC_LLC license will not be recognized unless the TAC_LLC.certificate is also installed (as shown in the following platform details display.

Licenses   TAC_LLC.license (TAC_LLC 3.6 - never expires)  TAC.license (Tridium 3.6 - never expires)

Certificates   Tridium.certificate (Tridium - never expires)  TAC_LLC.certificate (TAC_LLC - never expires)

Resolution

There are two ways to resolve this issue depending on network connectivity of the G3 Workbench computer.

  1. If public ethernet connectivity is available, the licenses and certificates can be downloaded from the I/A Series G3 (Tridium) license server, using the Workbench "License Manager".
    1. Open Workbench and connect to the subject ENC.
    2. Open the Platform then select License Manager.
    3. In the License Manager, select [Import] then check "Import licenses from license server".  This process will download any available licenses for the selected device, along with any available certificates.  After the download is complete, the licenses and certificates downloaded will automatically be installed. 
  2. If public ethernet connectivity is not available or the certificate is not found, download the TAC_LLC certificate from The Exchange Download Center.  Use Workbench to import the downloaded file.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6234
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.