EBO WorkStation freezes and crashes

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EBO WorkStation freezes and crashes
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2763 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EBO WorkStation freezes and crashes

Administrator CraigEl Administrator
‎2022-12-20 04:12 PM

on ‎2022-12-20 04:12 PM

Issue

Building Operation WorkStation freezes and crashes. The stack trace shows:

  • System.ComponentModel.Win32Exception: Not enough quota is available to process this command

Product Line

EcoStruxure Building Operation

Environment

Building Operation WorkStation

Cause

This is an error from Windows system:

  • Not enough quota is available to process this command

There are two potential causes for this error:

  1. Windows does not have enough virtual memory for all of the processes that are currently running on the machine or Windows is running out of other resources such as: disk space, handles, GDI resources, process message queue or something else. This error turns up on a lot of programs in Windows intermittently, such as Windows File Explorer.
  2. WorkStation freezes (usually because its waiting on the server) and the user tries to do a 'soft' shutdown (not a kill process) of WorkStation in the Task Manager. The Windows OS then sends instructions via the message queue (to simulate a user press on the "red cross" button on upper right in caption bar) which in turn leads to this quota error.

Resolution

If this error is seen, Microsoft recommends closing some applications and trying again. If you still get this message, increase the size of your paging file.

IncreasepageFileSize.png

 

  1. In the Taskbar Search, type “Advanced System“. You will see View Advanced System Settings. Click on it.
    • Or you can navigate to it via Control Panel
  2. In System Properties, click the Advanced tab
  3. In the Performance section click the Settings button
  4. Performance Options will open. Click the Advanced tab
  5. Here, under Virtual memory, select Change
  6. Uncheck Automatically manage paging file size for all drives
  7. Highlight your Windows system drive
  8. Select Custom size
  9. Change the Initial size value and the Maximum size value to a higher value
  10. Click Set
  11. Finally, Click Apply/OK all the way

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • CraigEllis22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore