Dual Power supply for automation server
  • Dual Power supply for automation server
Commander Chris_Asbury Commander
‎2020-10-02 08:12 AM
Last Updated: Crewman ContentModerator ‎2025-09-01 03:34 AM
Need for a dual redundancy power supply for the Automation Server.
EBO EcoStruxure Building Operation.
Building Operation Automation Server.
Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Understanding how to create a fail-safe power supply for an Automation Server.
To provide dual power redundancy to an Automation Server, a possible solution can be to use a Phaseo ABL4_ABL8RED24400.
This will allow the connection of two 24V PSU's to be connected to the inputs.
Then connect the output of the Phaseo ABL4_ABL8RED24400 to the AS's PS-24V
See the attached document and diagram for more information.
  • ChristopherAsbury20
100% helpful (2/2)