Issue
The option to download the application to a MNL-800 controller is not available in StruxureWare Building Operation Workstation.
Environment
StruxureWare 1.1 or higher
Cause
For the download option to be available the MNL-800 version must be 2.0.
Resolution
There are two options to handle this issue:
- Upgrade the controller board to version 2.0
- Treat the controller as a 3rd party LON device by importing the XIF file and handling the program in an external version of WorkPlace Tech.