Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Door supervised input trouble.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Door supervised input trouble.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1552 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Door supervised input trouble.

Picard Product_Support
‎2018-09-06 01:52 PM

Issue

For doors with long wire run to the controller it is very important to follow the recommendations as far as resistor tolerance and wiring distance and gauge is concerned.

 If a door still exhibits door switch trouble issues due to length etc. one possible solution is to use a resistance decade box to determine what value resistance should be used instead of the standard 10K ohms

Environment

AC1

AC1Plus

CX9702

ACX5740

ACX5720

ACX701

ACX781

Cause

Doors with extra long run to the IOU module / controller may produce trouble condition on the supervised inputs due to wiring issue; in some cases it may be necessary to replace the 10K ohms resistor with a different value to compensate for wiring.

Please follow the procedure outline below to determine the correct resistor value to use.

Resolution

If a door exhibit supervised input trouble issues due to wire length etc. one possible solution is to use a resistance decade box to determine what value resistance should be used instead of the standard 10K ohms, when doing this it is important the find the resistance value in the middle of the range, this will avoid random trouble due to temperature variations etc if the value happens to be right at the edge of the range.

To find the correct value use the following procedure:

  1. With the door closed start with the resistance decade box at 10K ohms.
  2. While monitoring the value of the input modify the resistance (either up or down) until the input reads CLOSED. Write down this resistance value. (VAL1)
  3. Continue to modify the resistance in the same direction until the input reads trouble again, write down this value. (VAL2)
  4. Pick a resistor value that is in the middle between VAL1 and VAL2 and use this value at the door instead of the standard 10K Ohms

NOTE: for series/parallel resistor type it may be necessary to use two decade boxes to find the correct resistance value.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5077
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore