Does the I/A Series (Niagara) R2 UNC-410 or the G3 ENC-410 support a BACnet MS/TP network?
  • Does the I/A Series (Niagara) R2 UNC-410 or the G3 ENC-410 support a BACnet MS/TP network?
  • sesa116868
    sesa116868
‎2018-09-06 01:44 PM
License form does not list the BACnet MS/TP driver.
I/A Series R2 UNC-410
I/A Series G3 ENC-410
License request for the UNC-410 or ENC-410 does not list an option for the BACnet MS/TP driver.
The UNC-410 / ENC-410 does not support any RS-485 drivers because the RS-485 port is not electrically isolated.
These controllers do support BACnet integration via BACnet-IP or BACnet-Ethernet.
If BACnet MS/TP integration is required, use the UNC-520 or ENC-520.
  • TAC IA Series