Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Does the ENC maximum number of LON bindings recommendation also apply to the JACE-6E, and JACE-7 platforms as well?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Does the ENC maximum number of LON bindings recommendation also apply to the JACE-6E, and JACE-7 platforms as well?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1139 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Does the ENC maximum number of LON bindings recommendation also apply to the JACE-6E, and JACE-7 platforms as well?

Picard Product_Support
‎2018-09-06 10:25 AM

Issue

Does the ENC maximum number of LON bindings recommendation also apply to the JACE-6, JACE-6E, and JACE-7 platforms as well?  The recommendation is not to exceed a total of 1200 bindings on the FTT-10 bus.

Environment

I/A Series G3, ENC and JACE controllers

Cause

LonWorks FTT-10 bus operation

Resolution

The number of bindings on an FTT-10 bus does not change regardless of the platform (e.g. ENC vs. JACE-6/7). The number of LON devices and overall number of bindings is somewhat arbitrary as the actual number is related to bandwidth limitations of the 78K FTT-10 bus.  The 1200 binding number is a general rule of thumb. This is the statement from an R2 engineering note that summarizes the basic issue.

---
A JACE controller provides a LonWorks FTT-10 port. Electrically, an FTT-10 segment supports up to 63 total nodes (addressable devices). Using repeater(s), a single LonWorks subnet can span multiple segments and have a total of 127 nodes.  However, in almost all cases, it is unrealistic to think that a JACE controller can “fully support” anywhere near 126 devices, because of bandwidth limitations.  The 78K baud FTT-10 bus can easily become “saturated” with too many messages (as a result of bindings).

Generally, most LON installations reach network saturation at around 1200 bindings (with average messaging). This can easily occur with far fewer than 126 devices. If connections are set to “poll-only," then the network could be sized to agree with the resource count limit of the JACE.  However, this configuration puts the JACE in the same category as most other LON interfaces, which poll for values (making for slow updates).
---

In summary, the actual number of bindings directly correlates to bandwidth, tuning, and acceptable data update rates.  An FTT-10 network can exhibit high bandwidth with less bindings or can be successfully operated at a higher number of bindings.  A good rule of thumb is that the average sustained bandwidth on the bus (as measured with a Lon Protocol Analyzer) should not exceed 25 to 28%.  This allows for message bursts to be successfully processed when needed.  In addition, care must be used when targeting a particular LON node with messages as the Neuron or host processor may not be able to process incoming messages causing lost and missed messages.  This includes the ENC or JACE which is why tuning of the individual LON devices is very important.

One alternative is to install two FTT-10 LON cards in the JACE-6E or JACE-7 and run two trunks. The LON network interfaces are configured as LON1 and LON2.  Purchase two cards and one driver. Remember to not overload the JACE (e.g. maintain good CPU and memory usage) which is good practice regardless of the communication interface.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 13189
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of