Does the DMS Ethernet NIM settings get saved with a DMS database 'backup' command?
  • Does the DMS Ethernet NIM settings get saved with a DMS database 'backup' command?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 10:19 AM
An installation has a DMS-3500 with an Ethernet NIM (Network Interface Module) and some MicroSmart controllers.  As part of a regular maintenance visit, a database backup is done.  What is considered a complete backup including the NIM's settings?
DMS
OPRIF 11.4 & 11.6
Database changes requiring a backup in the event a re-install is required
A complete DMS database backup typically involves two steps:  a backup of the DMS database and a backup of each individual MicroSmart controller database.
In addition, on an installation with ethernet NIMs, its configuration data is backed up as a separate step.
All three backup steps are done with OPRIF.
Note:  Echelon NIMs do NOT require backing up.
  • TAC IA Series
  • 13545