Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Does Niagara R2 provide a way to modify multiple objects property values all at once?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Does Niagara R2 provide a way to modify multiple objects property values all at once?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa116873_brid
    sesa116873_brid
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1144 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Does Niagara R2 provide a way to modify multiple objects property values all at once?

Picard Product_Support
‎2018-09-06 01:24 PM

Issue

Need to change the booleanKey property value from “overridden” to “value” for hundreds of GxBoolean objects.  Does Niagara R2 provide a way to modify multiple objects’ property values all at once without having to modify each object individually?

Environment

Niagara R2 (all versions)

Cause

The AdminTool object is a special "utility" apps object, available in the Local Library (tridium JAR file: tridium/apps/AdminTool). This object provides an admin-level command to "Search and Replace" property values for objects in the station database. Config properties define the property name to search, new value to write, plus other parameters for filtering and recursion. This operation automates what would otherwise be a manual process of opening and modifying multiple objects' property sheets.

Resolution

The setup is as follows:

  1. Copy the AdminTool app from the local library (tridium/apps/AdminTool) into the station.
  2. Double-click the AdminTool and select the Config tab
  3. Configure the AdminTool to change the GxBoolean objects’ booleanKey from “overridden” to “value”:
    • rootNode:                     /db/
    • ppropertyName            booleanKey
    • elelementName          (blank)
    • newnewValue                  Value
    • recurecurseChildre        true  (Setting to true will modify all proppropertyNameselected rootNode)
    • objecobjectTypeFilter     (leave blank- can be set to further filter)
    • nodeNanodeNameFilter    (leave blank- can be set to further filter)
    • PropertPropertyValueFiltereave blank- can be set to further filter)
  4. Right-click AdminToAdminToold selected searchAndReplace.

The GxBooleGxBooleansobjects’nbooleanKeyow be set to “value”.

Addition information can be found in the WorkPlace Pro Help menu located at Help > Index > General Index > AdminTool.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5972
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore