Does Niagara G3 provide a way to route alarms from multiple ENCs to the ENS, and then send emails alarms from the ENS?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Does Niagara G3 provide a way to route alarms from multiple ENCs to the ENS, and then send emails alarms from the ENS?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1573 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Does Niagara G3 provide a way to route alarms from multiple ENCs to the ENS, and then send emails alarms from the ENS?

Picard Product_Support
‎2018-09-06 01:00 PM

Issue

Does Niagara G3 provide a way to route alarms from multiple ENCs to the ENS, and then send emails alarms from the ENS?

Environment

Niagara G3,  all versions

Cause

NA

Resolution

The alarm generated in the ENC must to be forwarded to the ENS. The following are steps for accomplishing this. It is assumed that Email service is already configured in the ENS.

  1. Drag an AlarmClass object from the Alarm Palette to the AlarmService of both the ENC and ENS.
    These Alarm Classes are for alarms which will be emailed. Name both the ENC and ENS AlarmClass the same. Both names must be the same.
  2. Drag a StationRecipient from the Alarm Palette to the AlarmService of the ENC.
  3. Open the property sheet of the StationRecipient
  4. Select the ENS from the Remote Station dropdown list. (must have an established NiagaraNetwork connection) - Save
  5. In the ENC AlarmService, connect the Alarm output of the Alarm Class to the StationRecipient’s Route Alarm input.
  6. Open the NiagaraNetwork of the ENS and select the ENC NiagaraStation.
  7. Expand the ENC station and select Alarms
  8. Right-click on Alarms and select Property Sheet
  9. For Alarm Class, select “Use Existing” from the dropdown list - Save

Setup is now configured to send alarm email via the ENS

Note:
StationRecipient class receives Alarms and formats them for another station. The StationRecipient is available in the Alarm Module. This object along with AlarmClass will be used in this setup.

Alarms from a remote station are routed to any "matching" AlarmClass, that is, one with identical name as the "alarmClass" field in each alarm record. If no local "matching" AlarmClass is found, the station's default AlarmClass is used.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6741
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore