Does NC2/ACX2 need to be reloaded after changing its IP address from the configuration Web page?
  • Does NC2/ACX2 need to be reloaded after changing its IP address from the configuration Web page?
  • AbeMeran
    AbeMeran
‎2018-09-06 12:55 PM
Will NC2/ACX2 controller warm or cool start after its IP address is changed from the configuration web page?
or is it the case that the controller must be reloaded?
CX9640
CX9680
ACX5720
ACX5740
Function as designed
Changing the IP address or ACCNetId of a 9640/9680 or ACX5720/40 invalidates the backup in the controller's flash memory.
Controller will have to be reloaded from CyberStation after it re-starts.
  • 6892