Do not configure HTTP and HTTPS on the same port of a Xenta 511/527/913
  • Do not configure HTTP and HTTPS on the same port of a Xenta 511/527/913
  • SESA116857
    SESA116857
  • Sacco
    Sacco
‎2018-09-06 03:01 PM
Warning: Configuring HTTP and HTTPS on Xenta 511/527/913
  • Xenta 511
  • Xenta 527
  • Xenta 913
If the device reboots with both protocols set to the same port then it will become stuck in an endless reboot. The only way to correct this problem is to send the device back to the factory.
When configuring the HTTP (80 by default) and HTTPS (443 by default) ports in the Xenta 511/527/913 do not try to set these two protocols to use the same ports.