Displaying the actual value in an Vista Alarm text/email

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Displaying the actual value in an Vista Alarm text/email
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1259 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Displaying the actual value in an Vista Alarm text/email

Picard Product_Support
‎2018-09-06 02:31 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-28 06:57 AM

Issue

Show the actual value of the point being monitored in a Vista Alarm.

Example:

  • A temperature is monitored for a high temperature alarm
  • In the Vista alarm properties, under the Alarm tab, is "Text for Tripped Alarm" and "Text for Reset Alarm"
  • When the alarms trips, the Vista alarm queue should read "High Temperature of 77"

Product Line

TAC Vista

Environment

  • Vista Workstation
  • Alarm queue

Cause

The fact that an alarm has occurred can be enhanced by displaying the value that caused the alarm to trigger. For example, the room temperature at the time of the high temperature alarm. These values will then be recorded in the event log as well.

Resolution

  1. Enter the descriptive text into "Text for Tripped Alarm." In this example, "High Temperature of "
  2. Go to the Object tab in the Alarm Properties window and copy all of the text in the Object to monitor
  3. Go back to the Alarm tab in the Alarm Properties window and at the end of the descriptive text add an @ symbol and paste what you have copied from the Object to monitor. For example:
    High Temperature of @VISTASERVER-LTA-LNS-XG-AHU1-SUMMARY-R_T
    This will be displayed in the Vista alarm queue as:
    High Temperature of 77
  4. If it reads ??### instead of the value, add ".PV" to the end of the absolute path
    High Temperature of @VISTASERVER-LTA-LNS-XG-AHU1-SUMMARY-R_T.PV 

NOTE: the actual value may not be displayed in the Event window before Vista 5.1.7 (Vista 5.1.7 is included).

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3724
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore