Display the position of a return air damper on a Vista OGC graphic when using a common outside air/return air damper signal
  • Display the position of a return air damper on a Vista OGC graphic when using a common outside air/return air damper signal
‎2018-09-06 02:54 PM
How to display the true position of a return air damper on a Vista OGC graphic when using a common outside air/return air damper signal.
TAC Vista
  • TAC Vista IV
  • OGC Graphics Editor
If an outside air damper is interlocked with the return air damper, then there will only be one 0-100% value in the Vista database. Some math is required to calculate the inverse position of the opposite damper.
Entering the following formula in the Formula Section of the Attributes of a Digital Presentation:
C-100.00+C-1.00*
Note: the format for formulas in the OGC editor is Reverse Polish Notation.