Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Display options now the DCX250 is no longer available

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Display options now the DCX250 is no longer available
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2485 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Display options now the DCX250 is no longer available

Picard Product_Support
‎2018-09-06 09:17 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Issue

Display options now the DCX250 is no longer available

Product Line

Andover Continuum

Environment

  • Continuum
  • DCX250 Touch Screen Display part number 01-0008-300

Cause

The DCX250 is not available from January 2012: Discontinuation of Infinity 01-0008-300 (DCX 250) - PA-00184

Resolution

There is no direct replacement for the DCX250 and there is no other display that works directly on Infinet.

 

The Continuum display options are-

  • Netcontroller IO Bus - Infistat or LD-1
  • Direct connection to some controllers - Smart sensor or xP-Display
  • A Continuum Cyberstation could be used if more information and input is required.
  • Another option would be a Bacnet or Lon display.

Or, the L-VIS from Loytec using bacnet MSTP may be such an option (LonWorks and BACnet Touch Panels Release - PA-00106). http://www.loytec.com/products/lvis (LON via NC2-F- port16 would also be an option, see Can LONMark Devices be used with Continuum?) NOTE - All support for this product is via Loytec.


The EMX170 was a small display and keyboard available for some older Infinity Controllers (i1)
This unit is obsolete, although it may be possible to repair one. There is no replacement for this unit.
If the i1 controller is being replaced with an i2 unit then either a smart sensor or an xP Display plus room sensor could be used

Labels (1)
Labels:
  • Andover Continuum
Attachments
EMX170.zip
Tags (10)
  • Find more articles tagged with:
  • 2015
  • 22
  • 6441
  • dated
  • DavidChild21
  • ld1
  • lvis
  • oct
  • PaulFrost21
  • still
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore