Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Discrete Monitor (DM) and Discrete Control (DC) Points

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Discrete Monitor (DM) and Discrete Control (DC) Points
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513
  • SESA128071
    SESA128071

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1642 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Discrete Monitor (DM) and Discrete Control (DC) Points

Picard Product_Support
‎2018-09-07 01:18 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-09 01:22 PM

Issue

Discrete Monitor (DM) and Discrete Control (DC) Points

Product Line

TAC INET

Environment

I/NET Site

Cause

Explanation of Discrete Monitor (DM) and Discrete Control (DC) Points

Resolution

These points are always used in a pair. They control devices that would otherwise be controlled by an ordinary DO but are considered critical enough to warrant a DM/DC combination.

The DC point does the actual controlling (opening and closing of the hardware contact) and the DM point provides positive feedback from an external discrete device (for example, an air flow switch). The DM point is typically wired to a proof-of-flow switch that transitions when the controlled device is started or stopped.

It may also be used to monitor an auxiliary contact on a motor starter if a proof-of-flow switch is not installed. However, used in this way, the only information you are really receiving is that the contacts have closed or opened, but not whether the device is actually running.

Adding a resident DM point to a controller requires 30 bytes of memory.

Adding a resident DC point to a controller requires 37 bytes of memory.

When controlling DC/DM points using CU/PCU resident DDC, calculated points, or automatic temperature control (ATC), the Resident I/O Points editor entries of Scan Interval, Time to State, and Alarm Delay are very important.

Use the guidelines below to ensure that an alarm is correctly generated any time the DM point’s actual state conflicts with its respective DC point’s Expected State:

See Link Below

Regardless of which program is used, the time to state and alarm delay entries for the points should always be set large enough that the point being controlled is allowed ample time to change state (start, stop, etc.) before the point is declared to be in alarm. The DM point’s alarm delay value should always be set greater than the DC point’s time to state value.

In DCU/PCU resident DDC, the scan interval of the module should be set greater than the time to state and scan interval entries of the DC point being controlled.

When using a calculated point extension to drive a DC/DM pair, the DC point’s time to state should be less than the scan interval of the point.

When using ATC to control a DC/DM pair, it is important to remember that the point will always be issued a command by the program at the rollover of each minute. If the space temperature exceeds the cooling setpoint plus 1⁄2 the differential at 35 seconds past the minute, the DC point will be controlled ON in 25 seconds, again 60 seconds later, again 60 seconds later, and so on. When using ATC, it is recommended that the scan interval, alarm delay, and time to state entries all be set less than 60 seconds, allowing this alarm checking to be completed prior to the rollover of the next minute, when ATC issues its next command.

For further detail please use following link: DC-DM Operation.doc

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 1789
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore