Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Disable FTP in the Xenta 5/7/9xx Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Disable FTP in the Xenta 5/7/9xx Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • HenrikTarpgaard
    HenrikTarpgaard
  • sesa145087_brid
    sesa145087_brid
  • Anonymous user
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2186 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Disable FTP in the Xenta 5/7/9xx Controllers

Picard Product_Support
‎2018-09-06 01:39 PM

Issue

Disable FTP (File Transfer Protocol) in all X5/7/9xx controllers

Environment

Xenta 511, 527, 527-NPR, 555, 701, 711, 721, 731, 913

Cause

In some high security project installations, local IT groups require that FTP (File Transfer Protocol) be disabled on all devices within their network.

Resolution

  1. FTP into the Xenta 5/7/9xx controller by typing FTP://x.x.x.x (where x.x.x.x is the IP address of the controller) in the Windows Explorer address bar.
  2. Login with the root username and root password.
  3. Browse to the sys/system/ftp.cfg file and copy it to the desktop of the local machine.
  4. Open the ftp.cfg file with notepad on the local machine.
  5. Set the FTPMaxUsers="4" line to FTPMaxUsers="0" and save the file.
  6. Copy the file back to the FTP session on the controller and paste / replace it over the existing file.
  7. Logout of the FTP Session
  8. Cold start the controller

Now the Xenta 5/7/9xx controller will not have FTP access.

If there is a need to re-enable FTP please follow this steps on the Xenta 511, 527, 555, 701, 711, 721, 731, & 913

  1. Login into the controller via the web interface with the root level username and password.
  2. Navigate to Configuration > Servers > FTP Server
  3. Set the Max. number of users back to a valid number of 1-5 and click save.
  4. Cold start the controller.

If FTP needs to be re-enabled on the Xenta 527-NPR the only option will be to reload the system program. This is because the 527-NPR does not have a full web configuration interface like all other Xenta 5/7/9xx controllers to set the number of users.

 

Update note: In later versions of the Xenta Server, FTP is disabled by default (the number of users are set to 0).

If you still can't login to FTP, try to format the controller, reload the system program and try it again. Then it should work now.

Labels (3)
Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5504
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore