Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Digital outputs (V) on most Xenta 100 series controllers are ground sourcing (voltage sinking)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Digital outputs (V) on most Xenta 100 series controllers are ground sourcing (voltage sinking)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1322 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Digital outputs (V) on most Xenta 100 series controllers are ground sourcing (voltage sinking)

Picard Product_Support
‎2018-09-06 02:23 PM

Issue

In order to make the correct determination when selecting an actuator, it is important to first understand the difference between sourcing and sinking triacs.  A triac will act as a switch. By triggering its gate electrode, it will either conduct alternating current or impede it. While it can be thought of as contacts on a relay, it is important to note that it is decidedly different.

Environment

  • Xenta 121-FC, 121-HP
  • Xenta 101-VF, 102-VF, 102-ES, 100-D (legacy)

Cause

A digital output on a Xenta 121 (labeled V1 through V4) utilizes a ground sourcing triode for alternating current (TRIAC). In general, a TRIAC will either be voltage sourcing or ground sourcing (also referred to as voltage sinking). The Xenta 121 using ground sourcing TRIACs will be a determining factor when selecting actuators to be driven by digital outputs.

Resolution

A TRIAC output is similar to a hardware switch in that it will either open or close a circuit, allowing or stopping the flow of current.  Whether the internal side of the triac is connected to power or ground will determine whether it is a sourcing or sinking TRIAC.

If the internal side of the TRIAC is connected to power, as shown in Figure 1, it will be considered a voltage sourcing TRIAC.  When the output is activated, current will flow from the output, through the actuator, to ground.  Most actuators are designed to accept voltage sourcing outputs from controllers.


Figure 1. Voltage Sourcing Triac Configuration

If the internal side of the TRIAC is connected to ground, as shown in Figure 2, it will be considered a ground sourcing (or voltage sinking) TRIAC.  When the output is activated, current will flow from a power source, through the actuator, and into the output.  Some actuators are designed to accept both voltage sourcing and voltage sinking outputs from controllers. 


Figure 2. Voltage Sinking Triac Configuration

The digital outputs on terminals V1 through V4 of a Xenta 121 utilize ground sourcing triacs.  The G terminal between each pair of triac outputs sources 24 Vac.  It has direct continuity with the G power terminal.  When the output is active, the triac will conduct current to ground completing the circuit.

Said another way, if the output is inactive, there will be a 24V potential between V1 and G0 (ground), but a 0V potential between V1 and G.  When the output is active, there will be a 0V potential between V1 and G0, but a 24V potential between V1 and G.  An actuator is wired between V1 and G, so the potential across these two terminals will dictate whether the actuator is on or off.

In one example, a 3-wire floating actuator is wired with OPEN, COM, CLOSE connected to V1, G, V2 respectively.  There shouldn’t be a problem if the actuator is using the 24Vac signal to drive an AC motor.  When the open command is active, the actuator will see a 24V potential across its contacts and drive the motor.

In another example, a 4-wire floating actuator is wired in the same manner, but now also requires its own 24Vac power signal to run some on-board logic.  This example will not work because that actuator is expecting to see COM wired to ground, but it is in fact wired to the same 24Vac, resulting in 0V potential between power and ground of the actuator.

One solution is to use caution when selecting actuators to be driven by the Xenta 121.  Avoid actuators designed to be controlled with voltage sourcing outputs.  Another option is to use the triac outputs to close contacts on external relays that will source the necessary 24V as needed.

Another application of the digital outputs is to control the coil of a relay in order to open or close the circuit of another device, such as a low voltage terminal strip, fan motor contactor, etc. While some low voltage applications may function without the use of the relay between the 121 outputs and the device being controlled, this is generally not recommended and may negatively impact the reliability of the triac outputs.

Because the triacs are ground sourcing and G provides 24V power to the circuit, they can be wired directly to the 2 legs of the relay coil, as shown in Figure 3 below. Using this configuration, the triac is isolated from any harmful current that may travel through the external relay contacts.


Figure 3. Wiring Configuration for Relay Control with Triac

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4403
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of