Differences Between Tridium Jace 8000 WiFi and Jace 9000 WiFi

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Differences Between Tridium Jace 8000 WiFi and Jace 9000 WiFi
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1717 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Differences Between Tridium Jace 8000 WiFi and Jace 9000 WiFi

Guinan RandyDavis Guinan
‎2025-03-31 04:31 PM


Issue

Jace 8000 versus Jace 9000 WiFi specifications

Product Line

TAC IA Series

Environment

  • I/A Series N4 Jace 8000
  • I/A Series N4 Jace 9000

Cause

Defining WiFi feature differences

Resolution

The JACE 9000 includes a WiFi 5 radio supporting Bluetooth 5.2LE that is currently disabled.   Below is a table of the differences between the JACE 8000 and JACE 9000 WiFi:

 

Feature JACE 8000 WiFi JACE 9000 WiFi
WiFi Standard WiFi 4 (802.11n) WiFi 5 (802.11ac)
Switch Type Hardware Switch Software Switch
Modes Off, Access Point (WAP), or Client Off, Access Point (WAP), or Client
Security WPAPSK / WPA2PSK supported WPAPSK / WPA2PSK supported
Bluetooth Not Supported Yet Bluetooth 5.2 LE
WiFi Disabled at Factory Depending on SKU Depending on SKU

 

SKU Details:

  • JACE 8000:
    • JACE-8000-CSE-001 US
    • JACE-8000-CSE-002 WW
    • JACE-8000-CSE-003 NON WIFI
    • JACE-8000-CSE-004 China
  • JACE 9000:
    • JACE-9000-CSE-001 US, CA
    • JACE-9000-CSE-002 WW
    • JACE-9000-CSE-003 NON WiFi
    • JACE-9000-CSE-004 China
    • JACE-9000-CSE-005 EU

The JACE 9000 includes a button behind the door that can be configured as "Access Point Controlled" mode, enabling the use of an inactivity time limit for access point availability.  Selecting this mode activates a configurable time limit property for inactivity and the use of the Wi-Fi button to toggle on or off the Access Point availability.   This is similar to the hardware switch of the JACE 8000. 

 

Figures

  • Figure 1 shows the front panel of the New JACE 9000 WiFi
  • Figure 1.1 shows the JACE 8000 hardware switch indication
  • Figure 1.2 shows the JACE 9000 software switch indication 

Figure 1 - Front of JACE 9000 panel – WiFi LED and button locationFigure 1 - Front of JACE 9000 panel – WiFi LED and button location

 

Figure 1.1 - JACE 8000 hardware switch indicationFigure 1.1 - JACE 8000 hardware switch indication

 

Figure 1.2 - JACE 9000 software switch indicationFigure 1.2 - JACE 9000 software switch indication

 

NOTE: WiFi will not be supported in Jace 8000 with N4.15 release. Blackberry QNX chipset support has been dropped in the Jace 8000. Details and Summary 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • RandyDavis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore