Diagnosing Trends that are Storing Excessive Data
  • Diagnosing Trends that are Storing Excessive Data
  • Sacco
    Sacco
‎2018-09-06 10:32 AM
Diagnosis of a full Vista database shows that trend log storage size the culprit.
Vista trend logs
SQL database
Excessive trend logging can quickly fill a database.
This search will show both Xenta trend logs declared in Workstation/Menta and Vista Server logs.
  1. Search for ‘Type of devices or objects: Logical objects – Files – Trend Logs – Trend Log Vista’
  2. Set Property Value – Status – Equal to ‘On’
  3. Deselect the ‘interrupt if more than 1000 results’ if large Db with need for many logs.
  4. Once search populates right click on any result, Additional Property Value – Log space. This will add a column showing this setting in seconds.
  5. Sort column to identify any trends that are set to store more than the desired amount of values and could be causing issues.
Note: 604800 sec = 1 week
  • 12865
100% helpful (1/1)