Issue
When SigUpgrade is run at Release 4.08, a DeviceCnf.rec file that was created at Release 4.04 (as opposed to being the result from a SigUpgrade from Release 4.03) fails to upgrade to 4.08 correctly, and leaves the file unchanged in the 4.04 format.
Product Line
Satchwell Sigma
Environment
Sigma
Cause
Occasionally, at Release 4.04 when a new DeviceCnf.rec file is created it is tagged "Version 0" instead of the correct "Version 1"
Resolution
The DeviceCnf.rec file can be still be upgraded to Release 4.08 but by completing an intermediate upgrade from Release 4.04 by any one of following releases:
| Sigma Release | Build Number |
| Release 4.05 | 3.42.34 |
| Release 4.05 SP1 | 3.42.43 |
| Release 4.05 SP2 | 3.42.48 |
| Release 4.05 SEB | 3.43.18 |
| Release 4.06 | 3.44.14 |
| Release 4.06 SP1 | 3.44.16 |
| Release 4.06 SP1 | 3.44.18 |
| Release 4.07 | 3 45 48 |
| Release 4.07 SP1 | 3 45 51 |
| Release 4.07 SP2 | 3 45 58 |
Then finally upgrade again to Release 4.08.57 before continuing with the upgrade..