[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Schneider Electric PM710 Power Meter

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • [Dev File] Xenta 5/7/9xx Modbus RTU Integration to Schneider Electric PM710 Power Meter
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support
  • sesa115370
    sesa115370

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5238 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Schneider Electric PM710 Power Meter

Picard Product_Support
‎2018-09-10 11:40 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-21 05:17 PM

Issue

This article provides guidance on integrating the Schneider Electric PM710 Power Meter with the following Xenta controllers using Modbus RTU:

  • Xenta 511, 527, 555, 701, 711, 721 (Firmware version 5.1.5 and above)
  • Xenta 731, 913 (All versions)

Product Line

TAC Vista

Environment

  • XBuilder
  • Schneider Electric PM710 Power Meter
  • Xenta 5xx / 7xx / 9xx series controllers

Cause

Integration is required when PM710 Power Meters are used in systems managed by Xenta controllers via Modbus RTU. To support this, Product Support has developed a device template to assist with configuration. This template is intended as a starting point and may require customization to meet specific project needs. It is not a comprehensive points list.

Note: For assistance with template customization or troubleshooting, contact your local Schneider Electric Support team.

Resolution

To integrate the PM710 Power Meter with Xenta controllers using XBuilder, follow these steps:

  1. Download and Extract the Device Template

    • Download the .zip file containing the .dev file from the link below.
    • Extract the .dev file to a convenient location on your hard drive.
  2. Add the Device in XBuilder

    • Open your XBuilder project.
    • Right-click on the Modbus Master device.
    • Select Add Device.
    • Browse to the extracted .dev file and click Open.
  3. Configure the Device

    • Rename the newly added device to ensure it has a unique name within the Modbus Master network.
    • Adjust the device template as needed to match your specific integration requirements.

Downloads

  • Modbus Device Template – PM710 (.zip)
  • PM710 User Manual (PDF)
Labels (1)
Labels:
  • TAC Vista
Attachments
[Modbus Ext]PM710.zip
Tags (2)
  • Find more articles tagged with:
  • 7923
  • PeterLarsen25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore