Determining airflow (CFM) in the Xenta 102-AX

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Determining airflow (CFM) in the Xenta 102-AX
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2405 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Determining airflow (CFM) in the Xenta 102-AX

Picard Product_Support
‎2018-09-07 06:15 AM

Issue

  • Which values in the 102-AX plug-in affect the ultimate airflow reading output on nvoBoxFlow?
  • Formula for converting velocity pressure to flow.
  • Setting air balance parameters -- airflow coefficient, velocity pressure gain, offset, and cutoff, duct area, pickup factor and box constant.

Environment

Xenta 102-AX

Cause

Incorrectly configured boxes can cause erroneous airflow readings or unexpected behavior during calibration.

Resolution

The Xenta 102-AX uses a differential pressure sensor to convert velocity pressure values from 0-1" water column to a 0.25-4.0 volt output. The voltage signal is converted to a 10-bit digital value. The digital value is filtered and passed through the calibration gain and offset adjustments. Any value below the lowest velocity pressure threshold will be treated as 0"wc.

  1. Airflow_Sense.UCPTairFlowCoeff
    Airflow Parameters > Airflow Setting > Airflow Filter Coefficients (%)
    This value ranges between 0 to 99% where 0 is no filter and 99% is the maximum amount of filter. All process controls using the airflow reading use the filtered value. The default filter is 80%. The filter equation is defined as follows:
    display value = [previous display value * filter] + [new data value * (1 - filter)]
     
  2. Airflow_Sense.SCPTgain
    Airflow Parameters > Airflow Setting > Velocity Pressure Gain (multiplier/divisor)
    This value is multiplied with the raw velocity pressure reading to provide calibration gain to the final signal. The default gain is 10/10 (1). Resetting the box to factory calibration settings prior to calibrating the box will ensure that no invalid values are adversely affecting the operation.
     
  3. Airflow_Sense.UCPToffsetPress
    Airflow Parameters > Airflow Setting > Velocity Pressure Offset (WC)
    This value is added to the raw velocity pressure reading to provide calibration offset to the final signal. The default offset is 0. Resetting the box to factory calibration settings prior to calibrating the box will ensure that no invalid values are adversely affecting the operation.
     
  4. Airflow_Sense.UCPTpressCutOff
    Airflow Parameters > Airflow Setting > Lowest Velocity Pressure (WC)
    At the low end of the measurable velocity pressure, the sensor is inherently unreliable. The lowest velocity pressure threshold will zero out any value too low to reliably be measured. The default value is 0.016"wc. If airflow is reading 0 CFM despite the velocity pressure being above 0"wc, it may be that the threshold is set too high.

The calibrated velocity pressure value is used in the following calculation for airflow:
Airflow = Square Root(Velocity Pressure) * Duct Area * Pickup Factor -or-
Airflow = Square Root(Velocity Pressure) * Box Constant

The operator has the ability to enter the duct area and the pickup factor as separate values, or enter the box constant of the VAV terminal unit. The box constant is the duct area multiplied by the pickup factor. If the duct area or pickup factor is entered last, they will be used in the calculation. If the box constant is entered last, it will be used in the calculation. The pickup factor and box constant are sometimes referenced as the K-Factor(FPM) and K-Factor(CFM) respectively. This information must be taken from the VAV box itself and is usually displayed in a format such as the one shown below.

  1. Airflow_Sense.SCPTductArea
    Unit Parameters > Box Settings > Duct Area (sq feet)
    The cross sectional area of the duct in square feet. Most ductwork diameters are measured in inches. For round ducts, the equation for area is:
    • Area = π * [(d/2)/12]2 where d = diameter or
    • Area = π * (r2/ 144) where r = radius
    An 8" diameter duct would have a cross sectional area of 0.349 sq feet.
     
  2. Airflow_Sense.UCPTpickupFactor
    Unit Parameters > Box Settings > Pickup Factor (Imperial Units)
    This coefficient is provided by the VAV manufacturer and represents the feet per minute flow speed of the air at 1"wc of pressure. Typical values in HVAC VAV applications are between 2200 and 3300. Default value is 2950.
     
  3. Airflow_Sense.UCPTboxConstant
    Unit Parameters > Box Settings > Box Constants (Imperial Units)
    The box constant is the area multiplied by the airflow pickup factor.

Airflow is determined by multiplying the square root of the velocity pressure by the box constant. The final value is reported out the following SNVT:

  1. VAV_Controller.nvoBoxFlow
    Status > VAV Status > Airflow (CFM)
    This is the final airflow value in CFM as measured by the Xenta 102-AX. After calibrating the velocity pressure probe, the displayed value should match the flow values measured by a highly accurate magnahelic hood.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4619
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore