Determine IP address of Automation Server
  • Determine IP address of Automation Server
  • SESA116857
    SESA116857
‎2018-09-07 02:06 AM
How can the IP address of an Automation Server be determined if DHCP is being used
Automation Server
Building Operation Device Administrator
The setip command does not display the IP address when configured as DHCP.
To see the IP address of an Automation server connect to the device with a USB cable and start the Building Operation Device Administrator program. Right click on the AS and select the Network Settings option.
This will display the IP address in the Current IP address field.
The IP address can also be reached with additional statistics in the PuTTY interface (login is required) by using the ifconfig command.
The inet addr is the IP address of the device. This provides additional details such as bandwidth and problem packets.
  • 12390